The generator being installed is a 20kw, @83amps, with a 100amp breaker on the generator. The ats is service rated 200amp & the existing service is 200amps. Wanted to use table 310.15b7 which would be (al 2/2/2/w ground ser)from the generator to the switch. The problem I think I see is the code says to use this table if the conductors carry 100% of the load. I'm locking out misc loads such as the electric range,washer & dryer. So, with these loads locked out is this carrying 100% of the load or not???