I do voltage drop calculations regularly, no problem with the math. My question is when I do the calculation for a 3-wire 240 VAC circuit am I computing the VD between the neutral and a phase conductor or between the two outside phase conductors?
Example: 240 VAC, 43 Amps, 220', AWG 4 (uncoated) Copper
VD = (2 x 220' x .308 ohms x 43 amps)/1000 = 5.82 volts
VD% = (5.82/240) x 100 = 2.425 %
I'm thinking the answer is the two outside phase conductors, but I can't visualize it. Any insight is appreciated.
Example: 240 VAC, 43 Amps, 220', AWG 4 (uncoated) Copper
VD = (2 x 220' x .308 ohms x 43 amps)/1000 = 5.82 volts
VD% = (5.82/240) x 100 = 2.425 %
I'm thinking the answer is the two outside phase conductors, but I can't visualize it. Any insight is appreciated.