Hello everyone,
I am upgrading a building that previously didn't have any fire protection. There isn't a generator onsite and to comply with NEC I have to install a dedicated service to the fire pump. The service will come from a 12.47kv pole to an outdoor pad mounted 12.47kv-480v transformer before entering the building.
There will be 100 hp fire pump @480v, 3ph and a 2hp jockey pump @480v 3ph. I know per my calculations, the min. size the transformer should be is 150kva. However the code states that there needs to be a disconnect switch for primary OCD ahead of the transformer. My question is how do I do that if I'm coming off of a utility pole? Do they make disconnects within an outdoor transformer enclosure.?
This is the first time I'm doing a building without a backup generator onsite.
I am upgrading a building that previously didn't have any fire protection. There isn't a generator onsite and to comply with NEC I have to install a dedicated service to the fire pump. The service will come from a 12.47kv pole to an outdoor pad mounted 12.47kv-480v transformer before entering the building.
There will be 100 hp fire pump @480v, 3ph and a 2hp jockey pump @480v 3ph. I know per my calculations, the min. size the transformer should be is 150kva. However the code states that there needs to be a disconnect switch for primary OCD ahead of the transformer. My question is how do I do that if I'm coming off of a utility pole? Do they make disconnects within an outdoor transformer enclosure.?