mollydodger
Member
Installing a 600 ampere 240 volt single phase residential service. As I read this NEC reference and table it does NOT allow smaller conductors for services over 400 amperes. That said I assume the service conductors (from the utility to the CTS) must be sized par 310.16. I plan on pulling two parallel 350 plus one 350 neutral per leg for the service lateral. Once I am on the load side of the CTS I will be running to a 200 ampere transfer switch (service rated) and two 200 ampere service disconnects. I believe I can use 310.15 and the table for these conductor sizes as well as for feeders to my sub-panels as they are below 400 amperes. Am I correct?? Thanks in advance!!!