Section 110.14(C)(1)(A) says:
"Termination provisions of equipment for circuits rated 100 amperes or less, or marked 14 AWG through 1 AWG conductors, shall be used only for one of the following..."
(1) Conductors rated 60 degree C, etc....
If the circuit is rated 100 A or less then OK it makes sense that you must use the 60 degree C column from the conductor ampacity table. But, what does this mean marked 14 AWG through 1 AWG conductors? #1 AWG is rated for 110 A in the 60 degree C column. My question is, what is the point at which you can switch over to the 75 degree amapcity column: #1 AWG or 1/0 AWG if the terminals are marked for 60 degree C? The wording is confusing.
"Termination provisions of equipment for circuits rated 100 amperes or less, or marked 14 AWG through 1 AWG conductors, shall be used only for one of the following..."
(1) Conductors rated 60 degree C, etc....
If the circuit is rated 100 A or less then OK it makes sense that you must use the 60 degree C column from the conductor ampacity table. But, what does this mean marked 14 AWG through 1 AWG conductors? #1 AWG is rated for 110 A in the 60 degree C column. My question is, what is the point at which you can switch over to the 75 degree amapcity column: #1 AWG or 1/0 AWG if the terminals are marked for 60 degree C? The wording is confusing.