Duct and switch

Status
Not open for further replies.

jumper

Senior Member
I cannot think of an NEC off the top of my head, but besides the crushed duct, I do not see a proper heat sleeve for that wall penetration.

However, IMC 2009

603.11 Furnace connections.

Ducts connecting to a furnace shall have a clearance to combustibles in accordance with the furnace manufacturer?s installation instructions.
 

tonype

Senior Member
Location
New Jersey
I cannot think of an NEC off the top of my head, but besides the crushed duct, I do not see a proper heat sleeve for that wall penetration.

However, IMC 2009

603.11 Furnace connections.

Ducts connecting to a furnace shall have a clearance to combustibles in accordance with the furnace manufacturer?s installation instructions.

This install is ca. 1986
 