Bonding bushings

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
Where are bonding bushings needed coming to or from a transformer
Transformers are not part of the criteria for needing to use BBs.

The quick answer is service equipment and anything over 250V to ground, but the bonding requirement isn't limited to using only BBs.

See 250.97 for more info.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You might use one on the GEC if it enters the transformer enclosure but for the most part they're not required.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I seem to recall that the code used to require treating the secondary conductors/raceway of a transformer up to the first OCPD as service conductors for bonding purposes. Am I dreaming or possibly a senior moment?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I seem to recall that the code used to require treating the secondary conductors/raceway of a transformer up to the first OCPD as service conductors for bonding purposes. Am I dreaming or possibly a senior moment?

Actually we do treat transformer similarly (GEC size, bonding jumper size) but not with regard to bonding the raceway containing the secondary conductors. For some reason this concept of bonding bushings on transformers comes up very often on the job site.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Actually we do treat transformer similarly (GEC size, bonding jumper size) but not with regard to bonding the raceway containing the secondary conductors. For some reason this concept of bonding bushings on transformers comes up very often on the job site.

Same here. GEC size, bonding jumper, etc are similar to a service... but the raceway bonding before the first OCPD, I thought sure that it used to be there.
 