Wernermichael
New member
- Salt lake city, Utah, USA
Where are bonding bushings needed coming to or from a transformer
Transformers are not part of the criteria for needing to use BBs.Where are bonding bushings needed coming to or from a transformer
I seem to recall that the code used to require treating the secondary conductors/raceway of a transformer up to the first OCPD as service conductors for bonding purposes. Am I dreaming or possibly a senior moment?
Actually we do treat transformer similarly (GEC size, bonding jumper size) but not with regard to bonding the raceway containing the secondary conductors. For some reason this concept of bonding bushings on transformers comes up very often on the job site.
Same here. GEC size, bonding jumper, etc are similar to a service... but the raceway bonding before the first OCPD, I thought sure that it used to be there.
Maybe it was.