MTW wire used within control panels

Status
Not open for further replies.

eruotanen

Member
:?The usage of MTW wire is generally described as "within appliances". Several control panel builders I have worked with have designated MTW wire being used for internal control panel wiring as a normal practice; hence they will use #16 awg in a 15 amp control circuit within the panel rather than #14 which would be the case with THHN/THWN and similar conductors. Althought the NEC lists MTW as a wire type under 310.10 (B) and (C), I cannot fine ampacity and temperature ratings for MTW listed in the code as it was not listed in Table 310.15(B). Please advise where this can be found.
 