stuartdmc
Senior Member
- Location
- Newport Beach, Irvine, CA
A correction from the plan checker,
Add note to plan ?Service conductors within a building shall be encased in not less than 2 inches of concrete?, ?230.6.
This is what I have:
Within the main electrical room there is an existing 1200 amp UGPS, I am tapping out of the top of the UGPS running up and across the top with 4" emt to a 400amp meter section. the total run is 10ft. Does this really apply here? I know it is required if it runs under a building and or through a building if its coming from the street utility transformer. but not from the UGPS.
How would I comment back to the Plan checker on this?
Again Thanks for your comments
Add note to plan ?Service conductors within a building shall be encased in not less than 2 inches of concrete?, ?230.6.
This is what I have:
Within the main electrical room there is an existing 1200 amp UGPS, I am tapping out of the top of the UGPS running up and across the top with 4" emt to a 400amp meter section. the total run is 10ft. Does this really apply here? I know it is required if it runs under a building and or through a building if its coming from the street utility transformer. but not from the UGPS.
How would I comment back to the Plan checker on this?
Again Thanks for your comments