i was called to a customers house yesterday for a burnt out pool pump, long story short there is 130 volts on each leg of the service what do you guys regard as too much utility company tell me 130 v is ok
 

jumper

Senior Member
130V is a bit too high.

imagesqtbnANd9GcRe6H6cc6tqdv7QYnabjj_6mITKusjUJS7YTgkBVg8G0Qtc8Occ.jpg
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
No, was the voltage 220 or 260...
The poster stated the voltage was 130, but then stated the pool guy said the voltage at the pump was 220.

pool guy says pump was set for 220 pump outlet is 220

I think he meant the pump could be ran on either 120 or 240 (120 or 230) and the selector was set for 240 (or 230), and the receptacle for the pump was 240. In other words, the voltage rating at the receptacle was what was required by the pump at the higher voltage setting. But if he had 130V on each leg that would be 260V across the two.
 
Last edited:

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
i was called to a customers house yesterday for a burnt out pool pump, long story short there is 130 volts on each leg of the service what do you guys regard as too much utility company tell me 130 v is ok
130V on each leg measured how? Relative to what? Is the voltage at the service to the house phase to ground 130V off of both A and B phase?

Something is not adding up here.
 

formula1

Member
I think he meant the pump could be ran on either 120 or 240 (120 or 230) and the selector was set for 240 (or 230), and the receptacle for the pump was 240. In other words, the voltage rating at the receptacle was what was required by the pump at the higher voltage setting. But if he had 130V on each leg that would be 260V across the two.


Correct Sir. thank you
 

kwired

Electron manager
Location
NE Nebraska
POCO likely has a malfunctioning regulator on the primary side of their distribution system.

Did the motor burn up or an electronic control? The motor would likely handle 260 volts.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
If you have 130 (260) call the POCO. That is too high, plain and simple.
 

the blur

Senior Member
Location
cyberspace
I see 125/250 on a regular basis. 130 is pushing the upper tolerance. Light bulbs would burn out before a motor.

I also see 212-215 on a 208Y service.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I see 125/250 on a regular basis. 130 is pushing the upper tolerance. Light bulbs would burn out before a motor.

I also see 212-215 on a 208Y service.

Yea, +- 5% of nominal is our limit.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
No problems with anything else? Motors are the one thing that will take this extra voltage better than many electronics procucts will.

I see 125/250 on a regular basis. 130 is pushing the upper tolerance. Light bulbs would burn out before a motor.
Agreed. Like I said something is not adding up here.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I have seen voltage barely over 125V where I live, I have never seen normal voltage 130V phase to ground on both A and B. And then, why is the only thing that burnt up the motor? That would be the one thing that would survive an over voltage.

If the voltage coming into the house was 260V phase to phase to phase, 130V phase to ground, I would think something else in the house would have problems.
 