A sure way to avoid so called "Nusiance Trips"
The xo connection on transformer. I will look at that.
Curious to know what you found. Was the Xo bushing grounded on the 208V side of the transformer?
Make sure it is the ground fault function that is tripping the breaker. Usually transformer inrush will trip just the instantaneous overcurrent trip. Inrush should never trip the ground fault unless the inrush current is so high that it saturates the GF sensing CT's causing a false trip.
Is the 208V – 480V step up transformer a standard 480V to 208/120V transformer wired backwards? If so, is the 208 volt side neutral connected to ground or the panel neutral? If it is connected to ground circulating currents will false trip the service ground fault protection.
The 208 volt side transformer neutral must not be connected to anything. Just connect the phase leads (X1, X3, X3). Leave X0 floating.
Curious to know what you found. Was the Xo bushing grounded on the 208V side of the transformer?
Have you ever had your complete GF system tested? In particular I would be looking for neutral-ground bonds in downstream equipment.
How do you know it is the transformer causing the problem and not some other circuit?
Have you had someone look at the Time-Current curves for the GF device, the transformer inrush, and the other branches?
While an X0 connection on the 208V side of your step up transformer is not desirable, it should have no affect on your GF tripping.
The inrush current of unloaded transformers can be extremely non-sinusoidal, combined with a 'soft' utility supply (like you might have during a storm). Your GF device may not like these harmonics.
Why do you have GF protection on a 208V service?
But the first time. It was only the Transformer being engage if you understand what i've written. I know clarity is a key to people answering correctly.
I understand the first time you turned just the transformer on the GF tripped. As I said, energizing an unloaded transformer can really cause problems, especially if the GF is set to minimum values.
Other than that I cannot see where you have provided enough information for us to narrow down your situation. Although we have offered plenty of things to look at.
The most common problem in electrical systems is ground faults. Multiple small ground faults can 'pre-load' your GF relay such that is on the edge of tripping.