Senior Member
hypothetical question.

4 apartments -1 common area, 900 sq.ft each, common laundry, all gas heat- water-range, no A/C.

Main service disco, discos-sub meters-feeders to each apt and common area.

Apt load.

900sq.ft x 3VA=2700VA
2 SABC=3000 VA
HVAC load 500VA
Largest motor = HVAC=125% already added

5700VA-3000VA=2700VA

2700VA x .35 = 945VA

3000VA + 945VA + 500VA

total 4445VA/240V=19A

What size feeders and panel does apt need?

In short, are these feeders required to be sized to 230.79? 100 amps, 60 amps, or.....
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't feel 230.79 would apply to the individual units as they are directly supplied by feeders (not services). I see no minimun on feeders.
 

kwired

Electron manager
Location
NE Nebraska
hypothetical question.

4 apartments -1 common area, 900 sq.ft each, common laundry, all gas heat- water-range, no A/C.

Main service disco, discos-sub meters-feeders to each apt and common area.

Apt load.

900sq.ft x 3VA=2700VA
2 SABC=3000 VA
HVAC load 500VA
Largest motor = HVAC=125% already added

5700VA-3000VA=2700VA

2700VA x .35 = 945VA

3000VA + 945VA + 500VA

total 4445VA/240V=19A

What size feeders and panel does apt need?

In short, are these feeders required to be sized to 230.79? 100 amps, 60 amps, or.....

I did not go through details of your calculations but if 19 amps is all that is needed I don't see why you can't run a 20 amp feeder. Besides it would be fun to see how excited the inspector get when he sees it.:)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I spent the last hour trying to see how it would not be compliant and I haven't found a reason yet, :D
 