Different voltages spliced in same box
A few of the Foreman at work are stating you can not splice both 120 and 277 in the same box I can not find any thing in the code book that says you can not do this. If it is a violation what code article would it be?
roger
Fl
Retired Electrician
They are wrong, tell them they need to read 300.3(C)(1)
Roger
cadpoint
Durham, NC
It's not so much that you can splice the joints, it's the sum of the voltage in the box that causes the problem, it's 250V between conducts, you need separtation in the box!
I'm not sitting with a book!
roger
Fl
Retired Electrician
Jude, it's 300 volts.
Roger
hillbilly1
North Georgia mountains
Owner/electrical contractor
Roger
I have to take issue with that drawing, I may be missing something here, but since the 277 and 120 are separately derived systems, the voltage shown with the meter should not be the total of the two. Funny thing is in the 32 years of being an electrician, I don't remember ever checking between a 120 volt circuit and a 277 volt circuit. Looks like I got a project Monday morning. (and I probably just opened up a big can of worms that needs another thread)
infinity
New Jersey
Journeyman Electrician
There is a theoretical condition where, depending on the phasing, that the same two devices can have less than 300 volts between them. Maybe an engineer can explain it. :D
Hv&Lv
Engineer/Technician
I scanned over the threads and noticed that they say both systems come from seperatly derived three phase systems. How about a 277/480 three phase system and a single phase 240/120 system?
don_resqcapt19
Illinois
retired electrician
What would be the phase angle between the voltages on the two systems? Once you have that you use the law of cosines or other method of vetor addition to find the voltage between the two.
acrwc10
Master Code Professional
CA
Building inspector
You have all missed the forest while examing one tree. The OP said "splice differing voltages in the same box" not "Devices in the same box".
While you are correct you can not have the shown voltages on a device, in a box with switches and receptacles. You can SPLICE wires in the box, as long as the insulation on all the conductors is suitable for the to the highest voltage in the box. Since most wire used has a 600volt rating, if you have a J-box with 120 and 277/480 being spiced and then run to where ever, your good to go.
roger
Fl
Retired Electrician
See post #2
Roger
roger
Fl
Retired Electrician
Sorry Roger, I did and almost noted it. It was all the drawings that made me throw you under the bus too.:lol:
That's OK, I becoming pretty familiar with the undercarriage of the bus from people I work with. :D
Roger
All the drawings were an attempt to clarify what was incorrectly introduced in post #3. Post 3 was not really off topic but was incorrect information that could be taken as it was written to apply to OP.
acrwc10
CA
Building inspector
I agree, when a question is posted I think every angle need be looked at. I just wanted to clearify the most obvious to the OP. His "teachers/supervisors" were saying "you can't", when in some cases "you can" and he didn't say if it was in a j-box or a switch box so all points were valid.