Just getting my feet wet with Article 645 on requirements for Information Technology Equipment Rooms. Let's see if I have this right....
IF you meet the requirements for the IT room in 645.4 (disconnect, separate HVAC, occupancy separations with fire rated walls, etc.) THEN you can use the provisions of 645.
With respect to transformers, I take it that this means you don't have to follow the standard rules for grounding and bonding when the transformer is part of listed IT equipment.
SO- if they instal listed IT equipment with internal transformers that would ordinarily require the standard rules of grounding/bonding for transformers, BUT they don't meet 645.4 requirements, they is in violationland, right?
Point is, we don't know what kind of IT boxes/machines they are going to roll into the place after we final the TI permit, or at plan check, so how do we know to require the rules of 645.4?
Thnx :thumbsup: :thumbsdown: hmy:
IF you meet the requirements for the IT room in 645.4 (disconnect, separate HVAC, occupancy separations with fire rated walls, etc.) THEN you can use the provisions of 645.
With respect to transformers, I take it that this means you don't have to follow the standard rules for grounding and bonding when the transformer is part of listed IT equipment.
SO- if they instal listed IT equipment with internal transformers that would ordinarily require the standard rules of grounding/bonding for transformers, BUT they don't meet 645.4 requirements, they is in violationland, right?
Point is, we don't know what kind of IT boxes/machines they are going to roll into the place after we final the TI permit, or at plan check, so how do we know to require the rules of 645.4?
Thnx :thumbsup: :thumbsdown: hmy: