80 %

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
In what context are you speaking of an 80% factor? Nothing says you can't load a wire to 100%.
 

JDB3

Senior Member
In wiring a wall heater 4,000 watts @ 240 volts (actual voltage at site is 245 volts), would # 12 NM (romex) be acceptable? No central heat, so they may run continuous.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
In wiring a wall heater 4,000 watts @ 240 volts (actual voltage at site is 245 volts), would # 12 NM (romex) be acceptable? No central heat, so they may run continuous.

No, #12 is not acceptable. You are required to treat the branch circuit load as continuous by 424.3(B). You need a branch circuit breaker that is no smaller than 25Amps. You can't put #12 on the 25A c/b per 240.4(D).
 

templdl

Senior Member
Location
Wisconsin
wouldn't 4,000w/240v=16.67a? The 16.67=1.25%=20.83a which exceeds the rating of a #12 conductor it appears. As such is it #10 wire that should be used? #10 wire is rated 30a and you can use a 25at or 30at breaker to protect the wire.
 

97catintenn

Senior Member
Location
Columbia, TN
wouldn't 4,000w/240v=16.67a? The 16.67=1.25%=20.83a which exceeds the rating of a #12 conductor it appears. As such is it #10 wire that should be used? #10 wire is rated 30a and you can use a 25at or 30at breaker to protect the wire.

Yes, but you should probably explain why and where you found it info as to the 125% for the OP.
 

kwired

Electron manager
Location
NE Nebraska
Seems to be a few threads of similar topic recently.

You are going about this the wrong way. You do not pick the overcurrent device then the conductor and then see if that works with the load.

First thing to do is determine what the load is, as well as if it is continuous or noncontinuous. You then determine what ampacity of conductor is needed.

210.19(A)(1) tells us that minimum ampacity shall be not less than the noncontinuous load plus 125 percent of the continuous load. There is similar worded requirement for feeder conductors as well as service conductors.

Once you have minimum ampacity of conductor you can select overcurrent protection. 240.4 says that conductors shall be protected against overcurrent in accordance with their ampacities specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G).

If your conductor is already 125% of the load and you protect the conductor at its ampacity your overcurrent device will also be 125% of the load (or more if you were allowed to use next standard size higher).
 