Fire Alarm Panel - Fire Department

Status
Not open for further replies.
I would just like to know how fire alarm control panel in a building communicates to the local fire department. Is it a dedicated phone line that sends a unique signal to the fire dept.? What were previous methods used ?
 

nhfire77

Senior Member
Location
NH
I would just like to know how fire alarm control panel in a building communicates to the local fire department. Is it a dedicated phone line that sends a unique signal to the fire dept.? What were previous methods used ?

Everything Iwire said, plus UL listed celluar communicators and the most common is a (DACT) Digital Alarm Communicator/Transmitter over analog phone lines. 99% of those call a privately owned central station that contacts the local FD. Some FD's monitor dacts in house, but rare.

DACT's require regular (POTS) telephone service, which is in decline. DACTs via POTS are declining s....l....o....w...l...y to radio boxes, IP communicators cellular etc.
 

MichaelGP3

Senior Member
Location
San Francisco bay area
Occupation
Fire Alarm Technician
Some old(er) technologies not yet mentioned:

Reversing relays. Varitech and Keltron were manufacturers that made equipment to monitor these dedicated circuits. In my limited experience, these were monitored by both fire departments, police departments, and private central stations.

McCulloh circuits. In wide use prior to the advent of 2 line DACTs being approved for fire alarm monitoring, around 1984, as I recall. I have seen these monitored by private central stations and police departments (for fire alarm) on large university campuses.
 
Last edited:

MichaelGP3

Senior Member
Location
San Francisco bay area
Occupation
Fire Alarm Technician
There is another technology, whose name I'm not recalling, where a dedicated pair of wires handles the transmission of up to 5 distinct zones, based on differing frequencies applied.
 
Status
Not open for further replies.
Top