can the 2 pole 40 amp circuit for the blower heater be extended to the a/c compessor [using fused disconnect at the compressor]?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
IMO, no unless you make the 40 amp a feeder and the loads are appropriate. I suspect that a dp 40 has more than the blower. Art. 422.12 states central heating system shall be supplied by an individual branch circuit.
 