Fine stranded wire with into mechanical lug ( screw type) ..UL test ?

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
My point was that the NEC does not require terminations for finely stranded wire to be listed as was the original question.
110.14 in the 2011 code requires that they be identified for the purpose.
110.14 ... Connectors and terminals for conductors more finely stranded than Class B and Class C stranding as shown in Chapter 9, Table 10, shall be identified for the specific conductor class or classes.
Identified (as applied to equipment). Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Code requirement.

Informational Note: Some examples of ways to determine suitability of equipment for a specific purpose, environment,or application include investigations by a qualified testing laboratory (listing and labeling), an inspection agency, or other organizations concerned with product evaluation.


While the code rule says identified for the purpose and that falls short of actaully requiring it to be listed, there is no real way for the inspector to know it is suitable for the purpose by looking at the termination unless it is marked as suitable for use with finely stranded conductors. If it is so marked it would be listed for the purpose.




 

AKUMAR

Member
Location
INDIA
once fine stranded wire crimped into ferrule ..they canbe used inside mechanical lug.
why mechanical lug : reaon is that these lugs can be used with MCCB inside panel .



But he is not referring to a crimped lug, he said a MECHANICAL lug, and I think Don's point is that the mechanical lug listing makes no allowance for use with a crimp ferrule as a way around the restriction against using it with fine stranded wire. I agree, I don't see it either. UL, and local inspectors by the way, will want to see a specific listing that allows for this.

AKUMAR, is there some reason why you cannot just use a crimped lug? That's the way everyone else does it and if you use the correct lug and crimper, it will be a UL recognized method of terminating fine stranded wire. If you need to attach multiple cables, use bolt or stud terminals.

PS:
Actually, strike that part about local inspectors, they would not actually be involved because the Code does not allow the use of fine stranded cable like that at all! You can use it inside of a UL listed panel assembly and only in the manner accepted by UL, which as far as I know is only crimped lugs.

Read this for why.
http://www.iaei.org/magazine/2005/01/do-you-know-where-your-cables-are-tonight/
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I suggest crimp on pin adapters. These ones may not be the correct ones but you should be able to find them.


http://www.ilsco.com/ProductsDetail...pdU0DFKAA==&fjjfhjhj=pxSfT4xq9rrFSIQhsoRZrw==
As you noted they are for use with Class B and C stranded, he wants to use finer stranding than that. So not suitable for the use. I know of no crimp on pin adapters that go onto fine stranded wire, only lugs.

Besides, if you have to crimp anyway why not just crimp on the proper lug?
 

AKUMAR

Member
Location
INDIA
Below link shows pin are class B & C ..if I am able to find for class K wire as well .
Can I use these pins into mechanical lug then ?

Here I go tlot of question from members why I can not use compression lugs etc..

reason is --I already has mechanical lugs for breaker so i need to work around this only to get fine straned wire connetced to mecahnical lug.

Intially I think Crimping of wire is solution but now shape of crimp( square ,trapezoidal) can be a problem to insert into round hole of mechanical lug.


I suggest crimp on pin adapters. These ones may not be the correct ones but you should be able to find them.


http://www.ilsco.com/ProductsDetail...pdU0DFKAA==&fjjfhjhj=pxSfT4xq9rrFSIQhsoRZrw==
 

AKUMAR

Member
Location
INDIA
well ..lots of thoughts on compression lugs .
can anybody suggest a solution from any manufacturer to stack four compression lugs ( single hole) to one terminal ?
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Use normal stranded building wire from the CB to a Marathon Power Distribution Bolck. Connect the fine strand to the other side of the Marathon block.

If there is no room in the panel, you may need to mount a J-box adjacent to the panel.

Marathon Special Products makes PDBs that are rated for fine strand conductors.

ice
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
This (Shoo-Pins)will undoubedly solve the problem but the cost is very high . also need tool to operate die. cost wise not feasible

Yes, sometimes that is a problem.

Here is another solution:
Square D has a paper that describes wrapping fine strand conductors with copper foil. One then inserts the foil wrapped conductor in a normal strand rated mechanical lug.

It does work well. Although some (AHJs) say the paper only applies to Square D lugs. In which case, you are hosed. However, if not, my personal opinion is this is a good method, regardless of the name stamped on the lug.

ice
 

AKUMAR

Member
Location
INDIA
Could you send the link for product ..




Use normal stranded building wire from the CB to a Marathon Power Distribution Bolck. Connect the fine strand to the other side of the Marathon block.

If there is no room in the panel, you may need to mount a J-box adjacent to the panel.

Marathon Special Products makes PDBs that are rated for fine strand conductors.

ice
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
I am having this paper ..This indicate if we have to use sleeve we need to do UL tests .

Tell us why you feel the need to do any UL tests to use this sleeve method. Are you using a different design lug than SQD shows in their paper or a different manufacturer (but similar design) and think you must do tests such as those noted in the SQD paper? I'm completely lost on the purpose of any UL type of tests.

ice
 
Status