Wondering if anyone can help me solve this little mystery...
I have a client who recently bought a new panasonic microwave. After using it for about a week she noticed the bedroom circuit tripped occasionally. The bedroom circuit that is tripping is fed from an arc fault breaker, and it is on a completely separate circuit then the microwave. At first I figured it was simply coincidence but after about 50 trips now it has only ever tripped while the microwave was running (I witnessed this myself). Although the breaker doesn't always trip while the microwave is running, only occasionally. And the circuit the microwave is on never trips, although it is fed by a regular breaker rather then an arc fault, and is fed off of a GFCI receptacle on the kitchen circuit.
I measured the loads on the line and neutral for both circuits and I see nothing alarming, yet the breaker is still tripping. I thought perhaps there was a shared neutral somewhere and the microwave was sending some noise down the neutral causing a tripped breaker, but as far as I can tell both circuits are isolated from each other, until the panel.
I tested the microwave several times, each time I tested I let the microwave run for a bit, and about 1 out of 5 times it trips the breaker (iow I ran the microwave 5 times and one time the breaker tripped per test). I'm fairly convinced it is the microwave causing this but I just cannot figure out how?
The arc fault breaker is only a few years old, GE breaker. Tests fine. Loads are fine. Any ideas?
I have a client who recently bought a new panasonic microwave. After using it for about a week she noticed the bedroom circuit tripped occasionally. The bedroom circuit that is tripping is fed from an arc fault breaker, and it is on a completely separate circuit then the microwave. At first I figured it was simply coincidence but after about 50 trips now it has only ever tripped while the microwave was running (I witnessed this myself). Although the breaker doesn't always trip while the microwave is running, only occasionally. And the circuit the microwave is on never trips, although it is fed by a regular breaker rather then an arc fault, and is fed off of a GFCI receptacle on the kitchen circuit.
I measured the loads on the line and neutral for both circuits and I see nothing alarming, yet the breaker is still tripping. I thought perhaps there was a shared neutral somewhere and the microwave was sending some noise down the neutral causing a tripped breaker, but as far as I can tell both circuits are isolated from each other, until the panel.
I tested the microwave several times, each time I tested I let the microwave run for a bit, and about 1 out of 5 times it trips the breaker (iow I ran the microwave 5 times and one time the breaker tripped per test). I'm fairly convinced it is the microwave causing this but I just cannot figure out how?
The arc fault breaker is only a few years old, GE breaker. Tests fine. Loads are fine. Any ideas?