Feeder Panels

Status
Not open for further replies.

tomd53

Member
In our new plant being built the contractor has lighting panels 400 ft. from the main switchgear room. It is a 42 circuit panel with 38 breakers. My question is should the panel have a main breaker? It is protected in the main switch room but is a long way from the main switch.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Jim, a main is not required and this is a design issue. If your asking if this panelboard needs a disconnecting means the answer is no, it simply requires an OCPD which can located anywhere on the supply side of the panelboard including in a remote switchboard.

408.36 Overcurrent Protection.
In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
 

iMuse97

Senior Member
Location
Chicagoland
What determines whn a a MLO only is used as opposed to a MCB? Thanks

In a word, Code sets minimum requirements, but, as the above gentlemen mentioned, there may be design (engineered breaker systems) and/or convenience reasons why you may want an additional main breaker in a panel that is only required to be MLO.
 

renosteinke

Senior Member
Location
NE Arkansas
I agree, it's a design issue ... but, I wonder ....

Considering the various "70E" discussions, I suspect that an aggressive application would result in there not only being a disconnect next to the panel, but that it have an indicator light as well :(
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I agree, it's a design issue ... but, I wonder ....

Considering the various "70E" discussions, I suspect that an aggressive application would result in there not only being a disconnect next to the panel, but that it have an indicator light as well :(

How would NFPA70E require a 'local' main breaker?
Fixed visual indicators are typically not considered as meeting requirements for verification of the absence of voltage.
 