Derating conductors in conduit

Status
Not open for further replies.

KWH

Senior Member
There is no change from the 2008 code to 2011 concerning Table 310.15b 3a is there, #12 thhn can still be derated from the 90 degree column and have up to 9 ccc's and be on a 20amp breaker. I was told by someone they had an inspector stating you had to use the 75 degree column now.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There is no change from the 2008 code to 2011 concerning Table 310.15b 3a is there, #12 thhn can still be derated from the 90 degree column and have up to 9 ccc's and be on a 20amp breaker. I was told by someone they had an inspector stating you had to use the 75 degree column now.

Thanks

No change. You're correct. Once you exceed the 9 CCC threshold you need to go down to a 15 amp OCPD.
 