Marking Panelboards

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I'm not on the 2011, but noticed that 408.4(A) says that in all but one & two family dwellings, a panelboard is required to be marked as to where it's source of supply is. My question is, are industrial plants, commercial buildings, etc. required to mark what already exists? I know most code changes don't require changing already installed systems, but there would be little to no cost involved here. I know from experience that you could have dozens of MLO sub panels in a plant and not no where it is fed from. This is for sure one change I agree with. But is this change also "grandfathered" from updating?
 
Last edited:

jusme123

Senior Member
Location
NY
Occupation
JW
I'm not on the 2011, but noticed that 408.4(A) says that in all but one & two family dwellings, a panelboard is required to be marked as to where it's source of supply is. My question is, are industrial plants, commercial buildings, etc. required to mark what already exists? I know most code changes don't require changing already installed systems, but there would be little to no cost involved here. I know from experience that you could have dozens of MLO sub panels in a plant and not no where it is fed from. This is for sure one change I agree with. But is this change also "grandfathered" from updating?


. ................
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Engraved plastic plaques for this purpose can run up to $10 each. How many PNL's are there?;)

I said "little to no cost". I believe there were around 15. That would be a one time cost and could easily save lots more than that if you had to turn panels off and shut production down to try and find the source. I don't know what all would be an acceptable method of marking them, but even if there were none cheaper than $10.00 that would be worth it.
I still haven't heard anyone say if existing panels have to be brought up to code.
 

jumper

Senior Member
I said "little to no cost". I believe there were around 15. That would be a one time cost and could easily save lots more than that if you had to turn panels off and shut production down to try and find the source. I don't know what all would be an acceptable method of marking them, but even if there were none cheaper than $10.00 that would be worth it.
I still haven't heard anyone say if existing panels have to be brought up to code.

I believe existing panels are probably grandfathered.

You could easily buy blank labels and print the info on them. Stick them on the equipment.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I believe existing panels are probably grandfathered.

You could easily buy blank labels and print the info on them. Stick them on the equipment.

That's what I was thinking, but I don't have a 2011 to see what is acceptable. I imagine it probably just says marked, not sure.
 

jumper

Senior Member
That's what I was thinking, but I don't have a 2011 to see what is acceptable. I imagine it probably just says marked, not sure.

(B) Source of Supply. All switchboards and panelboards
supplied by a feeder in other than one- or two-family dwellings
shall be marked to indicate the device or equipment
where the power supply originates.
 
Status
Not open for further replies.
Top