answers to my post have dissapeared:cry:
however, I have another question. When can one use the "round up" method of determining the size of the conductors versus amperage with a generator? To be more clear.... can one use 500kcm conducors and fuse at 400 amps using the round up method from 380 amps?
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
on the load side of your generator OCP device you can as long as your calculated load does not exceed the conductor ampacity,
 