I have an HVAC unit with a MCA of 74A and MOCP of 90A. I have an existing 80A breaker I would like to use for this unit. How low below the MOCP can I size my breaker?
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I need clarification - 125% of 74A is 92.5A, which normally you would go to a 100A breaker. But, 440.52 says not more than, so 90A would match the MOCP. But the quandary is, I am not supposed to load a breaker to more than 80%, which in this case I am.

Is the NEC assuming that it will not run continuously? If so, that's a heck of an assumption. :confused:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I need clarification - 125% of 74A is 92.5A, which normally you would go to a 100A breaker. But, 440.52 says not more than, so 90A would match the MOCP. But the quandary is, I am not supposed to load a breaker to more than 80%, which in this case I am.

Is the NEC assuming that it will not run continuously? If so, that's a heck of an assumption. :confused:

The 125% has already been factored in 74 * 125% = 92.5. Just look at the nameplate and choose an OCPD between the MCA and the MOCPD.
 

anbm

Senior Member
MCA = minimum circuit ampacity = recommended conductor size?

I would get the actual motor full load amp (FLA) and size CB based on article 430.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
MCA = minimum circuit ampacity = recommended conductor size?

I would get the actual motor full load amp (FLA) and size CB based on article 430.


440.4(A) would require you to use the nameplate information.
 