History of GFCI requirements in the NEC


The GFCI was marketed in 1962 as a self-contained unit, to be wired in series with a load. The first circuit breaker type was introduced around 1968, and the first receptacle type in 1972.


1968 NEC * GFCI protection for underwater pool lights was required.


1971 NEC * GFCI protection was required for storable pools, for pool receptacles, and for some feeders. It becomes an option for protection of receptacles at construction sites.


1973 * required for outdoor receptacles at dwellings.


1975 NEC * required for receptacles in dwelling bathrooms, and for fountains.


1978 NEC * required for receptacles in dwelling garages; for bathroom and outdoor receptacles in mobile homes and recreational vehicles; for receptacles in recreational vehicle parks, marinas, and boat yards; and for receptacles in health care facilities.


1981 NEC * tub motors and portable signs were included.


1984 NEC * covered replacement receptacles, and also added hotel bathrooms.


1987 NEC * added receptacles in commercial garages, dwelling basements, and boat houses, spray washers, and receptacles serving kitchen counters near sinks.


1990 NEC * added photovoltaic roof arrays, receptacles serving kitchen islands, receptacles in crawlspaces, and receptacles near sinks in mobile homes and recreational vehicles.


1993 NEC * added receptacles in non-dwelling bathrooms, on rooftops, in elevator pits, and serving wet bar sinks in dwellings.


1996 NEC * added receptacles in trailers, receptacles serving escalators, electric vehicle chargers, receptacles in sheds, balcony receptacles, and receptacles serving previously exempt kitchen counters.

1975 NEC section 210-7, was the first year that all 15 and 20 amp receptacles in residential occupancies, were required to be the grounding type.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe GFCI was required in Bathrooms in 1975 but not until 1987 for kitchen counters within 6' of the sink. I think in 1996 it was required for all kitchen counter receptacles
 