cross building circuit?

Status
Not open for further replies.

anbm

Senior Member
Building A and B belong to the same owner. Each building has separate service.

Can we feed some branch circuits (20A/1PH, 120V or 277V) in building A from an electrical panel in building B? (because the panel in building B stays closer to the load). Thanks!
 

anbm

Senior Member
Thanks for the hint, this makes me wondering if the building has emergency generator as backup power source... then, should we need to have separate generator for each building or they can share one generator. 225.30 rule only address normal power service, I assume.
 

hurk27

Senior Member
Thanks for the hint, this makes me wondering if the building has emergency generator as backup power source... then, should we need to have separate generator for each building or they can share one generator. 225.30 rule only address normal power service, I assume.


You can use a single generator to feed two or more buildings, but you will have to use separate transfer switch's for each building.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don't see anything that says I can't have a service and a feed from a second building. In general, I can't have more than one of either, but I think the code permits one of each. The rules in 230 do not apply to feeds from a second building and the rules in 225 do not apply to services.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe 2011 allows it.

225.30 Number of Supplies. A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit. Where a branch circuit or feeder originates in these additional buildings or other structures, only one feeder or branch circuit shall be permitted to supply power back to the original building or structure, unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
 