From Mike's Master/Contractor Simulated Exam: part 3 q. 27

What's the general lighting and receptacle load for a 30,000 sq ft bank?

The answer key says to multiply the lighting load of 3.5VA/sq ft from the table by 1.25.

I got 135KVA but that's not one of the answer choices.

I thought Table 220.12 load was THE load. The question does not ask for feeder conductor size discussed in 215.2(A), or OCPD or Service for that matter.
 

jumper

Senior Member
Here is what I got:

T220.12

30,000 x 3.5 = 105,000

T220.42 and 215.2(A)(1)

105,000 x 1.25 =131,250 for lights

---------------------------------

220.14(K)

30,000 x 1=30,000

T220.44

30,000- 10,000=20,000

20,000 x .5= 10,000

20,000 for rec.
-----------------------------
131,250 + 20,000 = 151,250
 

Finite10

Senior Member
Location
Great NW
Thanks jumper.
I didn't use Table 220.44 for recepts because 220.14(I) says;
"except as covered in 220.14(J) and 220.14(K)..." (If I'm understanding that right)

My real issue is with adding a 'continuous' demand factor to a value given in a demand table for bank general lighting. I can see doing it if you were taking dwelling general lighting and using that value for a bank...
Dwelling is 3VA/sq ft
Bank is 3.5VA/sq ft
The extra 1/2 a VA is the continuous electric discharge lighting -I'd figure.

Annex D examples don't do that. Utilization, including use for 3+ hours, is figured into bank general lighting DF table value - I thought.

I understand that OCPD, service, and conductor sizing requires 125% continuous derating for ampacity.
 