From Mike's Master/Contractor Simulated Exam: part 3 q. 27
What's the general lighting and receptacle load for a 30,000 sq ft bank?
The answer key says to multiply the lighting load of 3.5VA/sq ft from the table by 1.25.
I got 135KVA but that's not one of the answer choices.
I thought Table 220.12 load was THE load. The question does not ask for feeder conductor size discussed in 215.2(A), or OCPD or Service for that matter.