jetlag
Senior Member
- Location
- Eatonton, Georgia
I want to be sure I am planning this right, I have 3 baths all are directly over each other , in a residence. basement , first floor . second floor . I plan to run 1 20 amp circuit for the gfic outlets in all 3 . I know when done this way can serve no other eguip outlets in baths, so lights will all be on different circuit. If I install any extra gfic outlets besides the ones by the basins , like a wall outlet 16" above floor, is that allowed to be connected to same 20 amp or does that count as serving other eguip ? people use them to connect small floor heaters. Also can you feed out of a bath gfci on one floor to protect bath on another floor or does each bath need seperate Gfci recepticals