Hi,
I was looking online for an answer and found your fourm. Hopefully you can help me.
We recently moved into a building that is supposed to have 200amps of 3wire 3phase 240V service to one of the meters. During last weekends storms we lost power. Upon inspection one of the pole mounted transformers had triped its safety. Not a big deal Utility people came reconnected it. but while I was waiting for them I noticed that the pole mounted transformers were two 10 Kva's and one 15Kva. By my calculation (35Kva x 1000 / 415.68V) those transformers would only provide 84.199 amps not the 200 amps we are supposed to be rated for. As we expand and add more equip. should I be concerned that we are really not capable of utilizing the full 200 amps as the utility company states in our service?
Thanks in advance for your help.
I was looking online for an answer and found your fourm. Hopefully you can help me.
We recently moved into a building that is supposed to have 200amps of 3wire 3phase 240V service to one of the meters. During last weekends storms we lost power. Upon inspection one of the pole mounted transformers had triped its safety. Not a big deal Utility people came reconnected it. but while I was waiting for them I noticed that the pole mounted transformers were two 10 Kva's and one 15Kva. By my calculation (35Kva x 1000 / 415.68V) those transformers would only provide 84.199 amps not the 200 amps we are supposed to be rated for. As we expand and add more equip. should I be concerned that we are really not capable of utilizing the full 200 amps as the utility company states in our service?