I am in the process of doing a design/build project for lighting up a couple of ballfields. We are looking at approx 80kVA of continuous load.
The problem we have is the utility transformer is 3 phase, 208Y/120 Volts, and is located 500 feet away. From the transformer to the panel, and then out to the poles and ultimately the fixtures, I calculated a voltage drop of about 20.3 Volts. On a 208 Volt supply, this represents a 10% drop.
Not acceptable in my opinion.
Upsizing the conductors to compensate for this is looking to be quite expensive, and I am considering installing a 112.5 kVA transformer to boost it up to a 480 Volt system.
Doing so would allow me to use smaller size wires, and put more fixtures on each branch circuit. The voltage drop calculations show I would be within 5% at the fixtures, an acceptable amount.
I have not installed many transformers "in reverse" as this would require.
I believe that using a standard "delta-wye" transformer would work, but there would be no neutral connection (X-0) for either the primary, or secondary.
A few questions come to mind for this:
Comments or suggestions are welcome.
The problem we have is the utility transformer is 3 phase, 208Y/120 Volts, and is located 500 feet away. From the transformer to the panel, and then out to the poles and ultimately the fixtures, I calculated a voltage drop of about 20.3 Volts. On a 208 Volt supply, this represents a 10% drop.
Not acceptable in my opinion.
Upsizing the conductors to compensate for this is looking to be quite expensive, and I am considering installing a 112.5 kVA transformer to boost it up to a 480 Volt system.
Doing so would allow me to use smaller size wires, and put more fixtures on each branch circuit. The voltage drop calculations show I would be within 5% at the fixtures, an acceptable amount.
I have not installed many transformers "in reverse" as this would require.
I believe that using a standard "delta-wye" transformer would work, but there would be no neutral connection (X-0) for either the primary, or secondary.
A few questions come to mind for this:
- I would certainly install a fused disconnect for the primary side (208) of this transformer. Would I need an additional one on the secondary side before my main breaker in the 480 Volt panel?
- Even though it is 500 feet away?
- Since the secondary would be "delta" 480 Volts, and no neutral conductor would be present, how does one perform the bonding/grounding? Does "X-0" get used at all?
- I am planning to install a 10 kVA 480-120/240 single phase transformer at the ball field pavilion building for incidental lighting and receptacle loads, including scoreboard(s). This would be a separately derived system, and make its own neutral.
Comments or suggestions are welcome.